Use these testing methods for certain supervisory devices

Click here to download as a Word document.

NFPA 72, the National Fire Alarm Code, outlines methods to test the following supervisory devices:

 

Q1

Q2

Q3

Q4

Control valve switches

       

  • Operate the valve
       

  • Verify a signal under one of the following conditions:
       

    • Within the first two revolutions of the hand wheel
       

    • Within one-fifth of the travel distance
       

    • According to manufacturer specifications
       
 

High- and low-air pressure switches

       

  • Operate the switch
       

  • Verify a signal when the required pressure increases or decreases a maximum of 10 lbs per square inch
       
 

Room temperature switches

       

  • Operate the switch
       

  • Verify a signal to indicate a decrease in room temperature to 40° F
       

  • Verify a signal to indicate a restoration in room temperature to above 40° F
       
 

Water level switches

       

  • Operate the switch
       

  • Verify a signal under one of the following conditions:
       

    • The water level raises or lowers 3 inches from the required level within a pressure tank
       

    • The water level raises or lowers 12 inches from the required level within a nonpressure tank
       

  • Verify a signal to indicate the restoration of the required water level
       
 

Water temperature switches

       

  • Operate the switch
       

  • Verify a signal to indicate a decrease in water temperature to 40° F
       

  • Verify a signal to indicate a restoration in water temperature to above 40° F
       
 

Waterflow devices

       

Flow water through an inspector's test connection

       

  • Verify a signal under one of the following conditions:
       

    • A flow of water equal to that from a single sprinkler of the smallest orifice size for wet pipe systems
       

    • An alarm test bypass connection for dry pipe, preaction, or deluge systems
       

 

Additional comments:______________________________________________________

________________________________________________________________________

________________________________________________________________________

________________________________________________________________________

________________________________________________________________________

________________________________________________________________________

________________________________________________________________________

 

Source: Based on information from Table 7-2.2 in NFPA 72 (1999 edition).




Subscribe Now!
Sign up for our free e-newsletter
Analyzing the Hospital Life Safety Survey

This book by former Joint Commission life safety surveyor Brad Keyes, CHSP, provides a practical, strategic approach to the life safety survey process. Keyes offers a room-by-room, floor-by-floor analysis of the life safety measures you need to have in place to avoid costly citations. He simplifies confusing Joint Commission standards and CMS requirements and reveals what you should be focusing on to pass your next life safety survey.